J Jim@HD Member Location West NY Feb 27, 2010 #1 Can there be more than one wire placed under screw terminal of the ground and neutral bars in a service panel?
Can there be more than one wire placed under screw terminal of the ground and neutral bars in a service panel?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Feb 27, 2010 #2 Jim@HD said: Can there be more than one wire placed under screw terminal of the ground and neutral bars in a service panel? Click to expand... Not if it is the grounded conductor, 408.41, and yes if it is the grounding conductor as long as the panel is rated for it. Most panels are rated for more than one wire.
Jim@HD said: Can there be more than one wire placed under screw terminal of the ground and neutral bars in a service panel? Click to expand... Not if it is the grounded conductor, 408.41, and yes if it is the grounding conductor as long as the panel is rated for it. Most panels are rated for more than one wire.