E2BRUCE
 - Grand Rapids, MI
I am preparing for the state of Michigan Masters Exam. While reviewing Example 8 I ran accross a few questions. The example given has 2-30 H.P. ,460V, 3-phase wound-rotor motors with a primary nameplate current of 38 A and secondary nameplate current of 65 A, with a temperature rise of 40 deg. C. I understand that the motor overload would be 125% of the nameplate rating, the example shows that as the 38 A for primary. 430.32(E) says that secondary circuits can be protected by the motor overload device. in this example would one always use the nameplate rating for the primary? With this type of motor likely to appear on my test, how would I select branch circuit short circuit protective device for these motors, is this based on the the primary's FLC or the larger of the two?
 Any help would be much appreciated.