I believe there is a section in the code that requires that #14AWG shall be protected by a breaker that is no larger than 15A, a #12 is protected by no larger than 20A, and #10 is protected by no larger 30A.
Is this a requirement for most applications? Does it matter what kinds of loads the circuits are serving?
For instance if I have a #14 being used for control circuits should it still be protected by a maximum of 15A?
Is #14 the smallest wire size that can be used to feed loads?
There is a rule, 240.4(D) off the top of my head but it does not apply to all circuits. Motors are type of load the rule does not apply to.
I believe there is a section in the code that requires that #14AWG shall be protected by a breaker that is no larger than 15A, a #12 is protected by no larger than 20A, and #10 is protected by no larger 30A.?
No Code section could ever be that simple :)
240.4(D) with exceptions. As Bob noted, motors for one.
Is this a requirement for most applications? Does it matter what kinds of loads the circuits are serving??
Most, but not all. see 240.4 1st paragraph
For instance if I have a #14 being used for control circuits should it still be protected by a maximum of 15A??
Normally. Some exceptions in Art 430 part VI
Branch circcuit consductors, yes, but other loads Not necessarily see 240.4