When sizing the cable to be connected between the drive chopper and the brake resistor is it simply a matter of taking the drives Max DC bus level and dividing it by the brake resistor value to determine the current through the resistor. This current can then be used to determine the wire size. So for example if the max DC bus level was 800V and the resistor value was 8ohms, then 10A would flow through the resistor and a #14, cable would be sufficient?
Is high temp wire typically recommended for this connection?
When setting up the brake resistor on the drive do you need to set the duty cycle of the chopper on the drive? Is this duty cycle set as a function of the duty cycle of the resistor? How is this value determined?