The water heater has two elements rated each at 240V, 4500W. The current reading draw is 18 amps with amp meter. The element resistance is 12.5 ohms each. Using ohms law the two elements resistance total is 6.25 ohms. The current should be E/R=I or 240V/6.25=38.4A. So that's about 19.2 amps per hot line. Question is aren't the elements supposed the cycle from top only to top and bottom elements together. I never noticed any difference in the amp meter reading to indicate any cycling.