Situation: Service rated ATS and the neutral is switched by the ATS Generator, 25 ft from the building, has a built in 1200 amp disconnect. Supply to building is in PVC.
On this job the 2005 Code applies.
The problem is that there is no equipment ground run with the phase condcutors from the generator. The engineer says they are not needed.
I first looked at it as simply a SDS. My first thought is we have to have an equipment ground , but then I considered the follwing:
Since the generator has a main, install a bonding jumper and electrode there and consider the supply to the building as a 250.32 feeder and since there is no metallic connection, bond the neutral at the building
(With that neutral bond the gen would no longer be an SDS and we will run that by the engineer,but I don't see that as a requirement)
Comments, please.
Comments, please.