I believe it depends on the height of the stack vs. the radius and height of the rest of the building. The 'cone of protection' will not cover anything above/beyond that cone.Can we protect only the stack?
We are upgrading boilers for an institutional ordinary structure and they mentioned they've had lightning stikes to the stack. We recommended a whole-building protection, but the client came back and said they wish for only the stack. NFPA 780-08 doesn't really define if only the stack can be protected without the rest of the building. Can we protect only the stack?
Protection is a misleading term to use, because what the NFPA 780 lighting system design performs is actually attracting the lighting.
That is actually a little misleading. The presence of an LPS or lack thereof does not induce, prevent, or in anyway effect whether or not a strike is to occur. In the event a strike is to occur, the LPS provides an attachment point and intentional path to and/or from the earth.
If that were true, than only buildings and structures with an LPS would be struck. And, buildings with an LPS would would always have strike attachment on the LPS..
But that is not the case is it? It is a common occurance for a highrise building to be struck along the side of the structure, rather than at the top. Smaller buildings a frequently stuck in the vicinity of much taller structures and surrounding trees..
In short, lightning is going to happen no matter what the conditions or circumsances are occuring on the earth. If and when that strike occurs, providing a path for the surge currents to flow is better than not providing one. There is no "hunt", lightning doesn't and can't seek out its target. End of story.