Jags252

Member
If i have a lug rated 1/0 to 500 mcm and i ran 600 mcm compact aluminum (for voltage drop) and the wire fits under the lug is it right??
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If it fit without trimming, I'd do it without a second thought.

May not be legally Kosher, but it's electrically sound.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I wouldn't do it even if it did fit. The lug is rated for a maximum condcutor size of 500 Kcmil. Anything larger, compact or not is a violation.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Then, the answer is to ask whomever will be inspecting it. If it helps, offer to show them a sample of the wire in a terminal.
 