Hi this is my first time so please excuse me for any errors. My scenario is
I am working with a compressor for a ice maker which has FLA 27amps and
the start capacitor has gone out twice in less than 6 months the voltage
is 208/230 single phase. the compressor is only 6months old. I checked the
incoming voltage it reads 210 volts phase to phase and 122volts to ground.
the compressor has built in overload protection and is fed with a 40amp
inverse time breaker which is also tripping. I megged the wires back to the panel
they were fine. we have A on sight HVAC tech he checked refrigeration it checked out fine. the relay also has gone out twice and the contactors look
a little burnt which leads me to believe that there has been high current. we have put an amp meter on during start up which reads about 23amps. so what would cause the start capacitor to go out? Capcitors are sized correctly we double checked.