Question on a 200 amp feeder???
jango
Distance: 325 ft. feeding a 200A rated sub panel with a total connected load of approx. 150 amps max.
Can someone recommend the minimum THHN copper wire size and PVC schedule 40 conduit size?
For "MINIMUM" 3/0-3/0-3/0-6awg in a 2 inch conduit. However, that is the minimum not accounting for an easy pull and voltage drop.