We were recently setting up a 480V 1hp Powerflex 70 VFD on a screw conveyor. After running the drive up to full speed we stopped the drive and as the drive was decellaring we noticed that the drive would trip on a "Deceleration Inhibit Fault". After looking in the manual for the cause of the fault is had to do with the DC bus voltage being too high. The DC level was around 730V DC when trip occured.
For starters we looked at the line voltage on the input to the drive and noticed that it was a little high around 500V L-L. This is because drive is on a new system that is not yet fully loaded. When sitting idle the DC bus voltage on the drive was around 690V DC.
When we would run the drive it would run up to full speed with no problem. When we gave it a stop command the drive would start ramping down with no problem, but when the drive go to around 15hZ the bus voltage would start to increase above 700V. When the drive finally got down to about 2Hz the drive would freeze at 2Hz for a while and the frequency would toggle back and forth around 2Hz until the drive finally tripped on the decel trip.
We tried increasing ramp down time, and had the same issue at 2Hz. The drive was in sensorless vector control mode when this happened. We changed drive to V/Hz and it made it worse, so we changed back to sensorless.
Finally after looking in the manual we found that one of the remedy's for this fault was to "disable the bus regulation" on the drive. After disabling the bus regulation this problem went away and we were able to ramp down the drive completely with no issues although the bus voltage would still go high around low speeds.
The other strange thing was that even when we were running the drive and ramped the drive down from 60Hz to 10HZ, the DC bus voltage would increase to around 740V at 10Hz and would not decrease even with the drive running the motor. As soon as we ramped back up to 60Hz this bus voltage decreased back down to 680V.
Any ideas what is causing this high DC bus level at low frequencies? Was disabling the DC bus regulation a good solution, outside of adding an external brake resistor?