if i have 4160v thats drawing 30 amps, what is the formula to calculate the amperage on the 600v secondary??....thanks
 
Assuming three phase primary to three phase secondary:
[(4160*sqrt 3)(30A)]/(600*sqrt 3)= 208 amperes
of course this can be simplified...
Remove the sqrt 3's for single phase to single phase transformers.
Simply P=IE with Pin = Pout...when using this with three phase don't forget to multiply the voltage times the square root of three.
 

jghrist

Senior Member
this tx is 30 years old, any idea what kind of % loss could be factored in..even a rough idea???
Very rough idea:
full load loss 1%
no load loss 0.3%

500 kVA transformer at 500 kVA load: 0.01*500 + 0.003*500 = 6.5 kW
500 kVA transformer at 250 kVA load: 0.01*(250/500)^2*500 + 0.003*500 = 2.75 kW
 