Hameedulla-Ekhlas
 - AFG
Frequency:
I remember I had studied frequency limitation to 3%. Is it right?
In UK and probably EUland supply frequency tolerance is +/-1%.Frequency:
That sounds like a lot of deviation if you are talking about the utility supply. I seem to recall that the US grid operating system works with a normal deviation of +/1 0.05hz.In UK and probably EUland supply frequency tolerance is +/-1%.
It is permitted deviation. Actual operating deviation is usually much less.That sounds like a lot of deviation if you are talking about the utility supply. I seem to recall that the US grid operating system works with a normal deviation of +/1 0.05hz.
It seems grid inter-tie metering would be affected by such variations.It is permitted deviation. Actual operating deviation is usually much less.
Why so?It seems grid inter-tie metering would be affected by such variations.
Because, from what I grasp, the grid-tied utilities buy and sell power based on metering the power flow, and vary this by adjusting the prime-mover torque, which seems would vary the relative frequency slightly.Why so?
Care to expand?
You can lead the grid every hour and still buy power. It depends on what the sum of your loads is doing. Most utilities do not have all their customers and generators located all in one isolated box. This was the case years ago, but now all of the grids are tied together.Because, from what I grasp, the grid-tied utilities buy and sell power based on metering the power flow, and vary this by adjusting the prime-mover torque, which seems would vary the relative frequency slightly.
In other words, they buy power by reducing their generation mechanical torque, letting their generators lag the grid slightly, and sell it by increasing the torque, causing their generators to lead the grid slightly.
I think it's lag and lead in terms for phase rather than frequency.In other words, they buy power by reducing their generation mechanical torque, letting their generators lag the grid slightly, and sell it by increasing the torque, causing their generators to lead the grid slightly.
One little distributed generation source is not going to change the system frequency. It is just pumping energy into the grid.Great discussion. Does anyone have experience with/knowledge about taking into account alternative energy being tied in at different points in case of distributed power generation? Would this just affect the overall scheme of lead/lag of the phase and result in the same system or are there more subtle differences?
You meter the output from the generators and you meter all of the load meter points. Your buys & sells are the net of those two.
Suppose you had all the generating capacity needed to serve your loads. In any given hour, you try to estimate what your load will be for the next hour. You schedule the generation accordingly. The amount you miss the actual load will determine your buys & sells.
If you had a little excess generation and no one was there to use it, the transmission grid had a higher voltage in that hour. If someone else needed that exact amount because they scheduled too little, the grid voltage stayed the same and the other guy buys your excess. If everybody over-scheduled (say a storm took out a section of the grid), somebody is going to have to back a unit down or the voltage on the grid will get too high.
The guys in the control area already have procedures in place to tell who's units will come on or off if things don't go according to plan. they also have procedures in place to tell who gets cut off if there is not enough generation to go around to maintain system voltage.
It is a lot more complicated than that but that is a simple way to look at it.
I was trying for slightly simpler.It is a lot more complicated than that but that is a simple way to look at it.
Agreed. Otherwise, there'd be no synchronization.I think it's lag and lead in terms for phase rather than frequency.
There has to be some web info on power system operations. I have a decent library, but I'll see if I can hunt up some online resources.Great explanation. A lot to learn here. Do you know where I can find information to read up on this?