Other than possibly higher neutral current how would non-linera loads contribute to this?
Why would you need more than one possiblity ?
Other than possibly higher neutral current how would non-linera loads contribute to this?
All typical real-world numbers. The test would be to see if the N-G voltage goes away with the circuits unloaded.The voltage to ground is 2.46 volts at 60 hz.
The main bonding jumper looks good and the GEC to the water main has 3.6 amps on it.
The whole service had 40 amps on the neutral at this time.
All typical real-world numbers. The test would be to see if the N-G voltage goes away with the circuits unloaded.
Make sure you've deenergized all circuits sharing that neutral. If the voltage is still there, then it must be present at the source panel. Check there next.The voltage is still thier with the breaker off feeding that circuit.
That means it's a relatively small voltage.I just need to add that the SPARK I,m talking about is a little spark.
During a project in our lab we saw a tiny spark between the ground and neutral conductors.
Any thoughts?
Does this mean you touched the neutral to the ground? If so, I would expect a spark. If you have 40 amps flowing back to the panel on the neutral, and you touch that neutral to a ground, a lot of that 40 amps is going to start flowing back to the panel over the ground wire, and any other ground paths available.
Steve
Make sure you've deenergized all circuits sharing that neutral. If the voltage is still there, then it must be present at the source panel. Check there next.
There should be some point where the voltage zeroes out. Definitely at a proper MBJ point, and maybe at sub-panel(s) farther downstream.
During a project in our lab we saw a tiny spark between the ground and neutral conductors. This building has a 3 phase 208 / 120 service and at least 70% of the load today is flourescent, (no A/C). When the students asked I felt it had to do with the non-linear loads in the building. We measered it to be 5 mA.
Any thoughts?
Go to photobucket. Open an account (it's free). Upload your pictures to photobucket. Use the link to the photobucket pictures in your posts.P.S. can anyone tell me how to put pics on the post and not as an attachment.
Is this circuit fed from the service panel? Is the neutral part of a mutliwire circuit?The voltage is still thier with the breaker off feeding that circuit. Also someone asked about ungrounded to EGC voltage and it is the same 2.46 volts
Also ungrounded to grounded is .2mV.
All these last readings are with the ciruit off.
You have created a crude switch. Any time you "switch" a circuit that is carrying current, there will be a spark. When the grounded conductor is touched to the grounding conductor you have created a parallel path for the current that was flowing on the grounded conductor. The size of the spark that is created when you switch a circuit is related to the amount of current being switched and the design of the switch.I just need to add that the SPARK I,m talking about is a little spark.
Make sure you've deenergized all circuits sharing that neutral. If the voltage is still there, then it must be present at the source panel. Check there next.
There should be some point where the voltage zeroes out. Definitely at a proper MBJ point, and maybe at sub-panel(s) farther downstream.
This circuit is feed from a sub panel off one of the main panels. the service is a 400 amp 208 / 120 volt with 2 200 amp panels.Is this circuit fed from the service panel? Is the neutral part of a mutliwire circuit?
Sorry I haven't gotten back on this sooner.
I have not been tried this yet. I'm having second thoughts about turning off a 400 amp main breaker to kill all power to see if I still get the same readings.
This circuit is feed from a sub panel off one of the main panels. the service is a 400 amp 208 / 120 volt with 2 200 amp panels.
The circuit feeding the lighting does not share a neutral with another circuit.
I was just hoping you guys can help me rule out my original thought of this being caused by harmonics due to non-linear loads.
Thanks
The voltage you are reading is the voltage drop in the neutral. when you touch the neutral to the EGC at the load end, you have just added the resistance of the grounding path to the neutral thus lowering the over all resistance, this is the spark you see, but this allows dangerous current to flow through the grounding and can cause a shock or fire hazard, this is why the NEC does not allow the grounding to carry current.
By theory you have just created a parallel path for the neutral current to follow, current will follow any path provided. Its impedence is much greater than the neutral, limiting the current.
Just my theory though.