e57
- San Francisco, CA
Trying to get a grip on the new California Title 24 Non-resi Energy compliance.... I feel as though I'm stuffing a hot needle in my eye...
Was there any editing on this stuff or too much? One could get so lost in the exceptions that they could find the change in the sofa but miss whatever this stuff is supposed to mean...
EXAMPLE:
EXAMPLE:
B. For all skylit daylight areas:
i. The skylit daylight area shall be shown on the plans.
ii. All of the general lighting in the skylit area shall be controlled independently by an automatic
daylighting control device that meets the applicable requirements of Section 119.
iii. The automatic daylighting control shall be installed in accordance with Section 131(c)2D.
EXCEPTION 1 to Section 131(c)2B
: Where the total skylit daylight area in any enclosed space is less than
or equal to 2,500 square feet.
EXCEPTION 2 to Section 131(c)2B
: Skylit daylight areas where existing adjacent structures obstruct direct
beam sunlight for at least 6 hours per day during the equinox as calculated using computer or graphical
methods.
EXCEPTION 3 to Section 131(c)2B
: When the skylight effective aperture is greater than 4.0 percent, and
all general lighting in the skylit area is controlled by a multi-level astronomical time switch that meets the
requirements of Section 119(h) and that has an override switch that meets the requirements of Section
131(d)2.
EXCEPTION 4 to Section 131(c)2B
: Skylit daylight areas where the effective aperture is less than 0.006.
The effective aperture for skylit daylight areas is specified in Section 146(a)2E.
C. The primary sidelit area(s) shall be shown on the plans, and the general lighting in the primary sidelit areas shall
be controlled independently by an automatic daylighting control device that meets the applicable requirements of
Section 119 and is installed in accordance with Section 131(c) 2D.
EXCEPTION 1 to Section 131(c) 2C
: Where the total primary sidelit daylight area in any enclosed space
has an area less than or equal to 2,500 square feet.
EXCEPTION 2 to Section 131(c) 2C
: Primary sidelit daylight areas where the effective aperture is less
than 0.1. The effective aperture for primary sidelit daylight areas is specified in Section 146(a)2E.
EXCEPTION 3 to Section 131(c) 2C
: Primary sidelit daylight areas where existing adjacent structures are
twice as tall as their distance away from the windows.
EXCEPTION 4 to Section 131(c) 2C
: Parking garages.
D. Automatic Daylighting Control Device Installation and Operation. Automatic daylighting control devices shall
be installed and configured to operate according to all of the following requirements:
i. Automatic daylighting control devices shall have photosensors that are located so that they are not
readily accessible in accordance with the designer’s or manufacturer’s instructions.
ii. The location where calibration adjustments are made to the automatic daylighting control device shall be
readily accessible to authorized personnel, or located within 2 feet of a ceiling access panel that is no
higher than 11 feet above floor level.
iii. Automatic daylighting controls shall be multi-level, including continuous dimming, and have at least
one control step that is between 50 percent to 70 percent of rated power of the controlled lighting.
EXCEPTION 1 to Section 131(c) 2Diii:
Controlled lighting having a lighting power density less than 0.3 W/ft
2.
EXCEPTION 2 to Section 131(c)2Diii:
When skylights are replaced or added to on an existing
building with an existing general lighting system.
iv Under all daylight conditions in all areas served by the controlled lighting, the combined illuminance
from the controlled lighting and daylight is not less than the illuminance from controlled lighting when
no daylight is available.
v When all areas served by the controlled lighting are receiving daylight illuminance levels greater than
150 percent of the illuminance from controlled lighting when no daylight is available, the controlled
lighting power consumption shall be no greater than 35 percent of the rated power of the controlled
lighting.
Mandatory except for the exceptions.....