Maurice Ibanez
I am being challenged by a contractor's Electrical Engineer who designed a motor branch circuit for a roll up door. The EE wants the contractor to install a 30 amp circuit breaker to provide short circuit and ground fault protection for a 115 vac 1/2 hp motor, with 8.2 amps FLA on motor data plate. NEC article 240.248 uses 9.8 amps for the computation. I have computed using an inverse time circuit breaker and come up with 20.5 and 24.5 amps respectively thus a 25 amp circuit breaker must be installed to provide short circuit and ground fault protection. The EE is currently trying to add additional loads from the motor control panel to the formula to get over the 25 amp hump since the have already purchased all the required breakers.
I have not found any documentation in the NEC that includes the control panel loads for computing short circuit and ground faults. Is there any articles that I have missed or any documents to support using or not using those loads.