I have a 400a 277/480v service.I have one 4in RGS going from the back of my outside POCO CT cabinet to the inside SE, ATS.
There will be 4 parallel sets in my conduit plus a ground.
Can I use the 90c column and parallel 250mcm, 290x2x70%=406a or do I have to use the 75c with 350mcm, 310x2x70%=434a. I'm thinking 75c because of the outside CT cabinet is in a wet location.
Also am I wrong to count the neutral ?
And I have to run a EGC to the CT cabinet, do I have to parallel a EGC or can I run one #3 to the CT cabinet? 250.122 (400a=#3 EGC)
My grounding will be done in the ATS with a 2/0 grn. 250.66 note1