Customer has 4.5kw dual element wh, has 10-2 mc in place, has 3-phase 208 service. Health department wants him to have more capacity he wants both elements wired to work same time on seperate stats. If i connect to 3 wire can i divide amps by 1.732? Most eco way to fix?
Plan "A" won't help. With just 2 elements even if you went to 3 phase, 1 phase would still be carrying 1 side of both elements...too much load at 4500 watts for #1.
(the elements are probably 4500 @ 240 and less at 208 (3300+ watts as I recall), but still too much for #10).
Also, wiring both elements to work simultaneously won't increase his capacity very much. It's still going to be "x" gallons of hot water available. It will decrease the recovery time so he would have more water available quicker but if he is running out during 1 use it's not going to help much.
On seperate t-stats AND seperate overloads (resets) also listen to Augies good advise.
Does the Health Dept. want more heating cap. or more gal. of water available. If heating cap both elements on at the same time will decrease recovery time as Augie said.38 gal per hour max at 4500 watt,less at 3800 watt. If gal cap. add a water heater or increase size. No cheap fix.
Augie
Would this be allowed? The unit is not being wired or operated per the MFG
specifications.
My point was that the unit is not designed to have both heating elements operating at the same time. Would that void any warranty. Also would this become a safety issue? The NEC requires the unit to be operated per MFG instructions.
Bob, Since they come factory wired so one simply connects to provided connection points, I'd say you were correct. At a minimum changing to both elements at once would be altering a UL (or other NRTL) piece of listed equipment.
As others post, running both elements at once wont noticably* increase the volume of hot water that can be obtained at one time, this is determined by the size in gallons of the tank.
Running both elements at once will however reduce the recovery time, and allow a greater useage in gallons per hour.
With a 3 phase supply, it should be possible to run 2 elements at once without overloading the wiring, provided that this was correctly sized in the first place.
With a 2 wire cable, the only option is to connect both elements in parralel, to the same phase, this will of course draw twice the amps, and overload a circuit intended for a single element.
If however a 3 wire cable is installed, to bring all 3 phases of a 208 volt supply to the water heater, then two elements can be utilised without any increase in current.
Connect one element between A+B and the other between B+C.
Although two elements are connected to the B phase, this conductor wont carry twice the current since the currents are out of phase.
Indeed, a third element could be connected between A+C , though that is of little use as most water heaters dont have provision for three elements.
Can the elements be replaced without replacing the tank ? UK ones can. If so it might be possible to install higher wattage elements, so as to fully utilise the ampacity of the existing circuit.
Another option might be to raise the themostat setting as high as possible, and fit a tempering valve to the outlet to avoid scalding.
This will in effect increase the storeage volume since say 25 gallons of near boiling water, if diluted with cold, might produce 50 gallons of water at utilisation temperature.
*To be pedantic, running both elements at once will VERY SLIGHTLY increase the amount of hot water that can be used at once.
To draw of the entire tank contents will take several minutes, and during this time more water is being heated, therefore a 25 gallon tank might provide 26 gallons of hot water, another gallon having been heated whilst the water was being used.
Doubling the loading will double the amount of water being heated whilst the water is being used, perhaps from one gallon to two gallons, therefore increasing the total amount from 26 gallons to 27.
The difference is unlikely to matter in practice.
Here in the UK I once fitted heating elements of 18KW in total to a relatively small hot water tank, this heated the water as fast as it could be used from a single outlet, and kept up with heavy use of 4 or 5 showers.
With a 3 phase 240/415 volt supply, the line current was only about 25 amps.
Most electric WHs have an overload cutout only on the top thermostat. Sounds like if the health dept. is involved they're trying to utilize a residential WH where a commercial WH is really needed.
there are plenty of times the elements are on simultaneously.
Its usually possible to change out the elements to get more heat.