Most every conduit around here fills with water. We have always pulled in THHN/THWN wire, is that the best for longevity / safety?
In general the more insulation the better depending of course on if or how water will affect the insulation. Conductors designed for direct burial will usually have thicker insulation than a conductor not intended for direct burial.
Protecting the insulation from damage during installation may be a big factor in how long it will last. Nicks and scrapes may go unnoticed and cause a failure later.
IMO XHHW would seem to be a better choice. Not from real scientific data just from using both XHHW and THHN/THWN.
In general the more insulation the better depending of course on if or how water will affect the insulation. Conductors designed for direct burial will usually have thicker insulation than a conductor not intended for direct burial.
I do not think I have ever seen large wires pulled in with out a few nicks and scrapes, usually just the outer layer of THHN, though sometimes a tad deeper :-(. It does not seem to matter if bell ends are in pull boxes and bushings on either end, somehow they scrape it on something, well, I should inclde "me" in "they"....so "we".
I am also looking at Type USE-2 (EPR-HYP) and Type USE-2 RHW-2 OR RHH XLP. Both approved for direct burial, is this going overboard? It may infringe on my conduit size, I only installed 4" and need 350MCM copper. It fits into kwired's suggestion for direct burial cable as well.
Well, of course it is. What else could it be?. . . you will have bulging insulation ... with nothing but white substance inside (probably aluminum oxide) . . .
Most every conduit around here fills with water. We have always pulled in THHN/THWN wire, is that the best for longevity / safety?
Well months ago we had a post which everyone said that that was not going to ever happen water can not come in if your conduit was installed correctly ?
And my post telling them that it happens all the time in florida thur pvc conduit you blow it out and the next day its back you just made my day thanks .
Well I think you remember things incorrectly.
Well I think if we go back and look at the thread we will see many said conduits are filled with water.
Freeze thaw cycles are a big issue if metallic conduit or concrete encased non-metallic conduits are used. The ice produces a crushing force that damages the insulation. I tried a number of code cycles ago to require underground conduits be installed like water pipe...below the frost line.you guys forgot to add that not only do they fill water they freeze solid as well..
Freeze thaw cycles are a big issue if metallic conduit or concrete encased non-metallic conduits are used. The ice produces a crushing force that damages the insulation. I tried a number of code cycles ago to require underground conduits be installed like water pipe...below the frost line.