sparky984

Member
It seems that underground installations for commercial projects from the utilty source to the first means of disconnect are always in conduit. Is this a code requirement? I have looked in article 300 and don't find this. Or is this a specification from the owner/electrical engineer?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
There is not an NEC requirement that service lateral conductors be installed in a raceway underground.

Take a look at 230.32 for the requirements for protecting service lateral conductors from physical damage.

Chris
 

RJH333

Member
Location
New Jersey
Underground Conduits

Underground Conduits

What are the depth requirements when running conduits under a building and in a slab of concrete weather in the slab on grade or in a tin pan deck. The first floor, and second floor are for parking.
 

mcclary's electrical

Senior Member
Location
VA
What are the depth requirements when running conduits under a building and in a slab of concrete weather in the slab on grade or in a tin pan deck. The first floor, and second floor are for parking.

You would have to ask the local POCO, as their requirements exceed NEC
 