Because of the potential for jamming.why does table 1 in chapter 9 restrict the conduit fill to 31% for two conductors and 40% fill for more than 2 conductors?
Thanks
. . . Exactly how the 31% figure was arrived at, I do not know...
I don't either, but I notice from the 50 and 65% fills you showed in the post referred to above, that 31 and 40% fills are each (about) 62% of the inner circles total areas, respectively.
Because it's not a third conductor of the same size. With two conductors the geometric maximum is two of equal (50%) diameter have a 50% fill.Thank you for the replies.
Smart,
Please explain the 50% and the 65% concept. i know i am doing something wrong on my math, because 2 conductors will fill 50%, but why the 3rd conductor only fills an additional 15%?
Thanks
If you want to get really technical, click here.