cschmid
- Northern cold country
Depends on the soil type but around here you would have to go 6 ft to be at frost level here water lines are at 8 ft to below frost line.
It's Min-a -snow-ta![]()
Most every conduit around here fills with water. We have always pulled in THHN/THWN wire, is that the best for longevity / safety?
I could at this point mention SWA (steel wire armoured) which I didn't think you guys have, but iwire metioned that it is available in the USA and used by PoCos.
This stuff is suitable for direct burial and wet conditions, and I'd have no hesitation throwing it into a lake; it'll survive better than any other cable I can bring to mind.
weressl,
That is good info. There are some insulations that I have encountered that are not covered by code, and ones that are that we most commonly use are isolated to a select few. It's good to know what else is out there.
While there are few frost issues and nil on ground water here, we have freaky 32 degree mornings and then 75 afternoons frequently in spring and fall and so condensation within conduits is normal. We find many older buildings with horizontal runs that are full of water within ceiling spaces that are dry areas. The temp changes are such that they have an adverse effect on conductors in conduit over prolonged time.
On old cable engineer once told me that the only waterproof cable jacket is lead, and even that will leak if it is damaged. Not sure if you can even buy lead jacked cable any more.
Back when the big multipair underground phone cables were lead sheathed, they had the cables pressurised with air to keep the water out, and had pressure alarms for when they started leaking.