We have a commercial grade range/oven. We have 208V going to unit. The nameplate says at 208V the unit draws 10.3KW. Thats 49.5A. Do we need to size the breaker at 55 or 60Amps and put in #6 conductor? NEC 220.56-Kitchen Equipment-other than dwelling units says the demand factor is 100%. now, we have someone telling us we are wrong and that we should take the 49.5A, multiply it by 80% which gives us 39.6A and OL should be 40amps.I decided to take this do a forum I trust. That is why I am asking you guys, what is correct?