Per 517.32 (H), in a Hospital, automatic doors for building egress are required to be on the Life Safety Branch.
However, for a nursing home (517.42), automatic doors aren't listed. Therefore, they are not permitted to be on the Life Safety Branch for a nursing home.
That seems odd. It seems like the exit doors would be equally important in both types of buildings. I'm wondering if not having the doors listed in 517.42 is an oversight. But surely, someone would have noticed by now.
Steve
However, for a nursing home (517.42), automatic doors aren't listed. Therefore, they are not permitted to be on the Life Safety Branch for a nursing home.
That seems odd. It seems like the exit doors would be equally important in both types of buildings. I'm wondering if not having the doors listed in 517.42 is an oversight. But surely, someone would have noticed by now.
Steve