I opened the panel on a new machine with multiple motors this morning. I noticed that all of the motor starters were set on auto reset. Why would they do this?
I opened the panel on a new machine with multiple motors this morning. I noticed that all of the motor starters were set on auto reset. Why would they do this?
I have never put one on auto, but I have been tempted. I have been out many dark and stormy nights resetting starters because of a power blip!
The auto reset only affects the overloads, and will do nothing if the starter drops out due to power sags.
The auto reset only affects the overloads, and will do nothing if the starter drops out due to power sags.
And you have to carefully consider the use of auto reset..in applications like conveyors or other machinery where an unexpected motor restart can cause injury or death if you change manual reset to auto reset you leave yourself open to severe liability.
I opened the panel on a new machine with multiple motors this morning. I noticed that all of the motor starters were set on auto reset. Why would they do this?
Sorry, but I disagree. A motor cycling on and off due to power blips will cause the overloads to trip.
Many conveyor applications I have worked on the things start and stop a lot on their own anyway.
Since they are suppsoed to be guarded to prevent accidentally getting maimed by one anyway, how would an unexpected start of the conveyor add any additional risk??
Its a great way for the manufacturer to make follow-up sales of new replacement motors after the originals burn up from constant restarting without proper troubleshooting.![]()
Possibly, but having the overloads auto-reset will NOT automatically re-engage the contactor, unless the control input is a maintained contact. In that case of course the motor would restart when power is re-applied. Which is still a possible serious safety hazard, if someone was trying to figure out why the motor had stopped in the first place.
Depends on the application. I make that statement based on a recommendation from a motor application guide, which mentioned a conveyor as one possible type of load that an unexpected restart would be dangerous.
Even in an application where a conveyor started on its own, what do think would happen if someone was working on that conveyor because it wasn't starting at all, when the motor overload suddenly re-engages?
There are literally millions of possible motor applications, and thus millions of reasons why/why not to use auto reset. Are we really gonna try to discuss them all in this thread? :roll::grin:
Many conveyor applications I have worked on the things start and stop a lot on their own anyway.
Since they are suppsoed to be guarded to prevent accidentally getting maimed by one anyway, how would an unexpected start of the conveyor add any additional risk??
With all due respect, this is a really bad way of pondering this. There's a big difference in a photo eye starting and stopping a conveyor through a PLC, and a motor starter that's gonna cool down and start up automatically about the time that someone starts looking at why it won't run.
Very dangerous and I agree with MX slick
Again it would only restart if the control is maintained contact.
If it is maintained contact the 'problem' is no worse than when a circuit trips or there is a power failure, as soon as power is restored the unit will start without notice. That is why we do LOTO before troubleshooting not after a lost arm.
That is why we have LOTA!
I appreciate your input, so don't get me wrong, OK?
What about an unmanned sewer plant? It seems that they have more power blips during storms ETC. than other facility's. I am on call 24/7/365. One of our worst plants is 40 miles from home. Computer/PLC controlled.
Beeper goes off 2 AM. I drag out of bed, log on and try to restart the pump or whatever isn't running. Won't restart. Drive 40 miles, check every thing out and everything is OK. Reset the starter, everything is cool. Drive 40 miles back, storm still raging, beeper goes off again........
Would that qualify for auto restart?
Possibly, but having the overloads auto-reset will NOT automatically re-engage the contactor, unless the control input is a maintained contact. In that case of course the motor would restart when power is re-applied. Which is still a possible serious safety hazard, if someone was trying to figure out why the motor had stopped in the first place.
Depends on the application. I make that statement based on a recommendation from a motor application guide, which mentioned a conveyor as one possible type of load that an unexpected restart would be dangerous.
Even in an application where a conveyor started on its own, what do think would happen if someone was working on that conveyor because it wasn't starting at all, when the motor overload suddenly re-engages?
There are literally millions of possible motor applications, and thus millions of reasons why/why not to use auto reset. Are we really gonna try to discuss them all in this thread? :roll::grin:
I assume you mean auto reset rather than auto restart - they are two distinct and different functions.What about an unmanned sewer plant? It seems that they have more power blips during storms ETC. than other facility's. I am on call 24/7/365. One of our worst plants is 40 miles from home. Computer/PLC controlled.
Beeper goes off 2 AM. I drag out of bed, log on and try to restart the pump or whatever isn't running. Won't restart. Drive 40 miles, check every thing out and everything is OK. Reset the starter, everything is cool. Drive 40 miles back, storm still raging, beeper goes off again........
Would that qualify for auto restart?
Many conveyor applications I have worked on the things start and stop a lot on their own anyway.
Since they are suppsoed to be guarded to prevent accidentally getting maimed by one anyway, how would an unexpected start of the conveyor add any additional risk??
The guy that got swept off the sweep chain 15 ft in the air could probably tell you. He was laid up for several months .