Not a direct violation, but a 110.3(B) violation if manufacturer's instructions do not include such a connection (which is quite likely).Is it a violation to install a nema 14-50R and only terminate the hot conductors. The circuit does not require a neutral.
I must concur. It could be destructive to provide a neutral terminal that isn't.
The first question is what type of plug is furnished with the equipment under consideration.This is for a peice of equipment not sure what it is located in a lab.
...
If unknown, the appropriate receptacle configuration would be a 6-50R (assuming a 208V or 240V circuit).
Smart show me a L6-50 device..
http://www.realpowerengineers.com/source/nema_l6-50r.htm
You'll likely notice that pictured is the L6-50P.
Now if you happen to be asking where you can buy one, good luck with that, as it seems no one currently makes or sells them![]()
Now if you happen to be asking wher...e=2&cvsfhu=3835373634" (Plumbers Surplus????)
First hit on google for "hubbell 6-50r": "http://www.buypowergear.com/detail.aspx?ID=4168" or even the 5th hit: "http://www.plumbersurplus.com/Prod/Hubbell-HBL9367-Receptacle/85764/Cat/1338?utm_medium=referral&utm_source=googlebase&cvsfa=63&cvsfe=2&cvsfhu=3835373634" (Plumbers Surplus????)
Now try to find an L6-50R...