We have several small motors for a new plant that we are finding to have low insulation readings. Most of these motors are in the 1hp - 10hp range. Some of the readings are below 1Megohm however others are around 5Megohm or so. The standard for the job is we only accept motors with readings 50Megohms or over, but I have a feeling that was written from someone who didn't know much about the subject.
I know as a rule of thumb that you dont want to energize anything reading less than 1Megohm however what about the ones where we are reading 5Megohms?
Even if we are getting low 5Megaohm readings, if we get a good DAR, or PI value should these still be o.k. to accept? What values would we want to see? I find it strange that soo many motors are reading low, and now we are either having to dry them out or replace them.
Would you say that for the ones less than 1Meg we should replace but the ones around 5Meg we should do second DAR or PI test for acceptance.
Also on a 6 lead motor we had on of the phases read 20meg to ground while the other two read 5megs to ground when wired in delta, but when wired in wye all three legs read 5megs to ground. What would cause this high 20meg reading when wired in Delta?