zappy

Senior Member
Location
CA.
When do you need to provide a 1/4" space? Anytime you mount equipment to brick or concrete? Would you use some washers to give you the 1/4" space? I've never been called on this before, but it sure would suck if you were, and had to take it all down!
 
312.2 only applies to cabinets, cutout boxes and meter socket enclosures installed in damp and wet locations.

So a basement wall may be a damp location is deem so by the AHJ.

But as 480 points out most panels have 1/4" spaces already built into their design.

Chris
 
also, from a Code standpoint, 300.6(D) requires 1/4 spacing for raceways and equipmemt where installed at indoor wet locations.
 
When do you need to provide a 1/4" space? Anytime you mount equipment to brick or concrete? Would you use some washers to give you the 1/4" space? I've never been called on this before, but it sure would suck if you were, and had to take it all down!

300.6 D
Indoor wet locations
Is one place I found it. I'm sure there are others.

Augie beat me to it! You may be older but you type faster! LOL
 