C Cow Senior Member Location Eastern Oregon Occupation Electrician Mar 25, 2010 #21 So, it's a new garage with rebar in the footings? But there is no CEE exposed. Somebody would be chipping concrete if that happened here....:roll:
So, it's a new garage with rebar in the footings? But there is no CEE exposed. Somebody would be chipping concrete if that happened here....:roll:
laketime Senior Member Mar 25, 2010 #22 Idaho is like the wild west still, and the slab was poured before we got the call.
T Tom C Member Location Maryland Mar 25, 2010 #23 Don't you need a 60A feed or is that just for service to separate building? Don't have the code book in front of me.:-?
Don't you need a 60A feed or is that just for service to separate building? Don't have the code book in front of me.:-?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Mar 25, 2010 #24 You would need a 60 amp disconnect. The feeder could be smaller. 225.39(D).