What section of the code is applicable?
There's not enough information to give a good answer. What ever you install, it must be listed for the area classification and comply with Article 500 & 502.
If ?controls" just mean a pushbutton station, install a NEMA 7 station with listed pushbuttons and the appropriate conduit seals at the correct locations. Or use a NEMA 4 box with factory-sealed pushbuttons listed for the area classification. If controls includes relays, or circuit boards, or motor starters or power supplies or ???, they have to be in a listed enclosure with proper seals.
A device?s suitability for use in a classified area does not depend on the operating voltage. We can't just say that it?s not hazardous because it?s low voltage.
Look at the web sites for Appleton and Crouse-Hinds or other manufacturers. They have some excellent tutorials on hazardous area installations.
Basically what I am referring to is a controller, and touchscreen panel which houses a circuit board with various 120V inputs and outputs. I'm trying to figure out what kind of enclosure I need to house this in.
The controller and touchscreen are in a NEMA 3R box. It looks like from reading 502 that as long as we put the controller and touchscreen in an enclosure rated for ClassII hazardout area (NEMA 7,8,9) then we will be o.k.
Does this sound correct?
That sounds a bit odd.
Why do you think so?
If you don't know what area you have, which is what I can gather form your description, you have no business deciding what equipment is suitable for either location.
We need to install a control box with only 120V controls in a hazardous class 2 area. What are the requirements for installing this box in this area?
What is the minimum NEMA enclosure that can be used? What section of the code is applicable?
Type 9 Enclosures constructed for indoor use in hazardous (classified) locations classified as Class II, Division 1, Groups E, F, or G as defined in NFPA 70.
Its odd because I don't think I have ever seen anyone do that before.
I am not suggesting it is a violation of some code, just unusual.
There is no reason a NEMA3R box cannot be used for that purpose, but they may not be well suited for it, especially in some styles.
From this site:
http://www.nema.org/prod/be/enclosu...=500&rdepth=0&sufs=0&order=r&cq=&id=4b4da2c87
Also, 502.10(B)(4).
Do you really have to install this in a Class 2 area? Is the area properly classified?
I'm out of town right now and don't have my code book, but I believe that section was saying the box needed to be rated for the location.Hmmmm...not exactly sure what you are trying to say or ask here.
The question was 2 part, 1-can the box go elsewhere? Does it really have to go in the Class 2 location? 2-Is the area truly a class 2 location? I've seen people claim areas were class 1 locations when in reality they were close to it and not really a class 1 area and I was just wonder if this might be similar.