mltech
- Ft. Lauderdale
Can somebody please clarify the difference between the two and why the new combos are required?
Thanks
Mike
Thanks
Mike
Combo AFCIs check for arc faults line-to-ground, line-to-neutral and neutral-to-ground (all parallel arcs). They also detect series arcing (within the same conductor).
Hence, they're considered safer.
Ok, I'm all for it, but why are they now required over the older AFCI variety code wise?
The old ones, AFAIK, did not detect line-to-neutral and neutral-to-ground arcs, nor series arcs. Only line-to-ground. But keep in mind, I'm not 100% sure on this.
As for why they're required, I'm sure it's in part due to the fact that it was the manufacturers that submitted the Proposal.![]()
They are required because that is what the original proposals for AFCIs said the AFCI could do. The non-combo ones could never do what was promised in the original proposals for the 1996 code (proposals that were submitted on or before the first Friday in November of 1993). It took the manufacturers some 13 years to produce the product that they said they had available in 1993.Ok, I'm all for it, but why are they now required over the older AFCI variety code wise?
As far as I know the AFCIs have always had a 30 to 50mA ground fault detection circuit. That would open the circuit on a line to neutral or neutral to ground fault.The old ones, AFAIK, did not detect line-to-neutral and neutral-to-ground arcs, nor series arcs. Only line-to-ground. But keep in mind, I'm not 100% sure on this. ...
Boy, they just keep finding ways to make the job pricier.
So only combo afci's in new residential construction? Can't wait to try it with lighting control...
What code are you working under?
I'm curious to know why that would matter? Combo's in 05 too right?
"Why do I have to use the new Combo AFCI breakers"
Nobody has yet to give a clear answer. I understand they offer better protection...
And I know the code says...
Well, if those two reasons don't do it for you, then I'm not sure what kind of reason would convince you![]()
I think an argument could be made that in the case of an existing installation, replacement of a defective Branch/Feeder AFCI with a new Branch/Feeder AFCI would be allowed. Other than that, if AHJ's aren't enforcing the code, Branch/Feeder AFCI's will be installed and supply houses will continue to sell them.I guess I should have said, why are they still selling the old ones?
You raise a very good point here and I agree completely. It is important that AHJ's strive to enforce the code correctly and consistently in order to keep the playing field level for the electrician that wants to do it right.Also, I think the lack of communication and acceptance of the code by AHJ's could cause some grief.
As I witnessed what happened to a fellow electrician in Miami.
The AHJ would not accept the older AFCI's and made them change 5 panels worth of breakers. I have a clear understanding of how these combo's work just not a clear understanding of how this is being enforced. We do work all over the state of Florida and this could make a large $ difference from county to county. And could price me out of work on new bids...
And thanks to all who chimed in on this...