We as a plant had an analysis to our electrical equipment and had the switch gear labeled . What should we do to be complaint with OSHA? Will we get doucumention on the survey? What else is required for us ?
We as a plant had an analysis to our electrical equipment and had the switch gear labeled . What should we do to be complaint with OSHA? Will we get doucumention on the survey? What else is required for us ?
Thanks zog for your list. When I get to go back to the plant this will come in handy for the workers . We are always talking about electrical work when I am there ,they just had a survey, no one else knows about all these steps they need to do in the electrical safety program. I like this.
For the vast majority of all existing MCCs, a fault in one of the buckets will propagate onto the vertical bus in that section. Most studies list a single incident energy value for all of the vertical sections, although some will include a separate value for the line side lugs of an integral main device.On the mcc there are 2 labels 1 on each end of the mcc, does this mean the label applies to any bucket work is performed in ? I am told they don't use the tables anymore because they had a study completed there, is this so? I also read or seen it somewhere about the annex in 70e that the sections are suggestions and not something that is required to be followed, I see some form like permits and presedures are labeled in annex sections , I thought that the permits were required when working energized ?
We as a plant had an analysis to our electrical equipment and had the switch gear labeled . What should we do to be complaint with OSHA? Will we get doucumention on the survey? What else is required for us ?