Therefore, if X1 is connected to X3, then X2 and X4 are in phase and the voltage difference between X2 and X4 is zero.
If X2 is connected to X3, then because of the known phase relationship the X4 to X3 voltage is added to X2 to X1 producing an X4 to X1 voltage double the voltage X2 to X1.
Because of the series connection you used, X1 to X2-X3 to X4, and the known phase relationship the voltages added, meaning got larger.
I agree.
But if you were to use the series connection X1 to X2-X4 to X3, then the voltages subtract, and the difference between X1 and X3 is zero.
Consider:
V2 = V1*sin t + V1*sin t = 2*V1*sin t
V2 = V1*sin t - V1*sin (t+180) = 2*V1*sin t
V3 = V1*sin t - V1*sin t = 0
V3 = V1*sin t + V1*sin (t+180) = 0
So if adding produces a larger result, then subtracting and doing a 180 deg phase shift of one sin function produces the same result.
Definition of reference points and and voltage points is all important in defining phase relationship.
What is the maximum possible phase shift with an RC network?
Consider this:
A center tapped secondary, a first diode anode connected to X1 and a second diode anode connected to X4, both cathodes are connected together, and a load resistor from the cathodes to X2-X3. What is the output?
Next a single diode from X1 to a load resistor to either the center tap or X4. What is the output?
After this change the transformer so X2 and X4 are the "center tap". Now what is the result?
With two diodes and a load resistor I have created a circuit that can tell if there is a phase difference between two sine waves of equal amplitude and frequency.
It is also possible to build a phase measurement circuit using zero crossing and slope detection components.
A phase is a description of the relationship of one waveform to another not a particular transformer connection.
I can build a transformer with single phase input that produces an output that is phase shifted from the input by an angle that is not simply 180 deg out of phase. Simply by adding a shading coil to the transformer core.
jim:
If X1 and X3 are reference points, then X2 and X4 are in phase.The two 240V voltages are X1->X2 and X3->X4. They are in phase, based on industry convention.
When they are connected in series they remain two in phase voltages of X1->X23->X4, with a single resultant additive voltage of 480V.
I agree.
Consider:
Consider this: