I have been unable to find in NEC,NFPA 70B or Stalcup's a requirement for periodic torque on switch gear for a facility. Is there a rule of thumb or did I completely miss it?
The reality is that re-torquing is not required and may even be a bad idea.
Roger
The reality is that re-torquing is not required and may even be a bad idea.
Roger
I have been unable to find in NEC,NFPA 70B or Stalcup's a requirement for periodic torque on switch gear for a facility. Is there a rule of thumb or did I completely miss it?
This manufacturer wants re-tightening:
This manufacturer wants re-tightening:
![]()
Why is this?
A sticker installed in the 70's is a far cry from a standard. But if they insist use the right torque values.
Yep, Cover Your Assets.
Don't you just LOVE the 4 different notices and warnings? It does not yet include the labels, tags and warnings to be placed by the installer and the user. Talk about ADD?!![]()
70's?
________
I dunno, looks old, I don't work with anything that small so am not sure what it is.
New AC unit sitting on the floor waiting to be installed. Photo is from 2010.![]()
The practice I like is to torque at installation, then using a sharpie or similar put a line that indicates alignment between the nut and bolt. Then all that is necessary is a visual inspection to verify that the nut has not moved. You can do the visual inspection just before you shoot the IR camera.
And that has what to do with the OP about switchgear? Your sign is refering to wires and terminals, not switchgear bus connections.
How do you know what the OP is asking? Switchgear could mean the enclosure, I didn't see any mention of busses. He could be asking about busses or terminations, we don't know do we?
Roger
How do you know what the OP is asking? Switchgear could mean the enclosure, I didn't see any mention of busses. He could be asking about busses or terminations, we don't know do we?
Roger
Could be, once again, we really don't know do we?What do you mean switchgear could mean the enclosure? Are you suggesting he is asking about torque specs for the covers or something?
And you may very well be right, but he could very well be asking about terminations.I'll bet you a bumper sticker he is asking about the bus connections.