- Logan, Utah
code ref please???:-?
It's not a violation to have one located there, it's just that the receptacle can't be counted as the required countertop receptacle.
Check out 210.52(C)(5) Exception to #5.
Chris
210.52(c)(5)
I?ll agree with that.IMO, this is open to interpretation.
I?ll agree with that as well.I say (think) you could have a flat island, with one pop up receptacle on top, and 12" of overhang everywhere.
I do not agree here. And as I said, I seem to recall that this has been debated before. The essence of my point of view is that the code language is not written in the manner of, ?at least one must be this way, and you can do what you want with the rest.? Rather, the language is written along the lines of, ?receptacles shall be located here, except that in limited circumstances you might be able to put them there.? There is no opening in the language to allow ?extras? to go anywhere we want. If there is a receptacle, it must go in the place the code says to put it.It doesn't mean that a receptacle cannot be placed under the overhang, but it means that that receptacle that is placed under the overhang more than 6",cannot be counted as the required outlet. . . . Underneath you could put 35 receptacles fed from 15 amp circuit, all the way around the island and be compliant.
It doesn?t say that. It says receptacles go here, and that is all it says. There is a reason for the 6 inch limit on the overhang. The reason has to do with safety, with legs and knees bumping into cords and spilling hot coffee pots on laps. That reason does not disappear, if you put the ?required? receptacle on the countertop surface itself, then add one ?extra? receptacle under a 12 inch overhang.The requirements are for the SABC.
I applaud you for using common sense and having the nads to make a decision based on reason rather than fear.
a receptacle located below a counter top that extends more than 6" beyond its support base is a violation and should have failed, no exception
As an inspector do you make judgement calls? Or do you follow the 'letter' of the law?
There is NO contractor that can build to code, and if you find him let me know, it is impossible.
This is the first thread, that I have read, that has people using common sense.
Just being a common guy I look at the FIRST sentence in the code.
90.1(A) Practical Safeguarding.
I like the word 'practical'.
What does practical mean to you guys?
A lot of fun tomorrow, as in practical jokes.What does practical mean to you guys?
look at 90.5 (A), and 210.52 (C) exception says shall not, common sense tells me that does not comply and fails inspection
Please tell me where it says the outside edge of a countertop.
Drilling a hole or cutting a slot creates an inside edge to the countertop.
Again this should be approve. And the OP has used good judgement.
I?ll agree with that.I?ll agree with that as well.I do not agree here. And as I said, I seem to recall that this has been debated before. The essence of my point of view is that the code language is not written in the manner of, ?at least one must be this way, and you can do what you want with the rest.? Rather, the language is written along the lines of, ?receptacles shall be located here, except that in limited circumstances you might be able to put them there.? There is no opening in the language to allow ?extras? to go anywhere we want. If there is a receptacle, it must go in the place the code says to put it. It doesn?t say that. It says receptacles go here, and that is all it says. There is a reason for the 6 inch limit on the overhang. The reason has to do with safety, with legs and knees bumping into cords and spilling hot coffee pots on laps. That reason does not disappear, if you put the ?required? receptacle on the countertop surface itself, then add one ?extra? receptacle under a 12 inch overhang.
While it may be against code, I'm for it as a common sense solution. On the one hand, the NEC isn't supposed to be a design guide
it not a may be against code it is against code, unless your state or town has an amendment to that section you have no choice but to enforce it as written, if you don't like it, put in a code change proposal, this has nothing to do with a design issue it is a required receptacle.
Well, that is not entirely true. The second paragraph of 90.4 gives the AHJ the authority to permit alternative methods. If the AHJ feels that drilling a hole in the counter top as described in this thread achieves equivalent objectives to the code prescribed method, then this alternative may be permitted.
Sub-section (C) only refers to outlets for countertops. Has nothing to do with wall or floor receptacle outlets, they are covered by 210.52(A). Fine to have others below the counter.I think it is a violation to have one there. But I also think this has been debated here before, with no clear consensus on the outcome. :roll:
Well, one could be an individual circuit for a refrigerator, and the other 34 would need to be switched. Otherwise, no 15 amp receptacle SAB circuits in food rooms.I wanted to make sure we were reading the same section. IMO, this is open to interpretation. It doesn't mean that a receptacle cannot beplaced under the overhang, but it means that that receptacle,,,that is placed under the overhang more than 6",cannot be counted as the required outlet.
Under neath you could put 35 receptacles fed from 15 amp circuit, all the way around the island and be compliant. The requiremnts are for the SMBC. IMO
The ability to be safe would exist then. Again, (C) is only for countertop outlets. If one was 30" below the counter a standard 24" appliance cord wouldn't reach anyhow.... There is no opening in the language to allow ?extras? to go anywhere we want. If there is a receptacle, it must go in the place the code says to put it. It doesn?t say that. It says receptacles go here, and that is all it says. There is a reason for the 6 inch limit on the overhang. The reason has to do with safety, with legs and knees bumping into cords and spilling hot coffee pots on laps. That reason does not disappear, if you put the ?required? receptacle on the countertop surface itself, then add one ?extra? receptacle under a 12 inch overhang.
Pretty much. No building wired to code either.There is NO contractor that can build to code, and if you find him let me know, it is impossible.
Written permission.yes by special permission (whatever that means),
Because it has been assured that an equivalent level of safety would be obtained by allowing the proposed altenative installation.is that like double secret probation, why would anybody grant special permission
True, one can always find a means to comply. They could have added an angle bracket to extend the support base to within 6"or a written variation would be required in my area and i can tell i would reject it, i would never sign my name to that, makes no sense there is always a way to comply with that section
True, one can always find a means to comply. They could have added an angle bracket to extend the support base to within 6". Compliant, but may not be better.