periodic torque of switch gear
zog
Charlotte, NC
Could be, once again, we really don't know do we?
Roger
Since when do facts get in the way of our discussions? :) I have a feeling this is one of those dead end threads where the OP never comes back.
That being said, if this is for connections in switchgear and the decision to torque is made the right values should be used.
iwire
Massachusetts
But the question remains, are you saying that upon installation these should be checked or are you saying as a yearly exercise?
zog
Charlotte, NC
They should be torqued at installation and checked by the commisioning test engineer. After that I recomend testing them with a microhmeter during maintenence inspections.
iwire
Massachusetts
So the answer to the OPs question ....
I have been unable to find in NEC,NFPA 70B or Stalcup's a requirement for periodic torque on switch gear for a facility. Is there a rule of thumb or did I completely miss it?