Good day,
I have an existing hospital with an emergency generator nameplate rating of 75 KW and 260 amps. Monthly test show a peak of 210 amps recorded via facilities. 1 ATS with no separation of life safety, critical, equipment. 1 EM distribution panel that feeds everything. 1970 construction.
The Hospital has been forced to add a sprinkler system per the State. No domestic water available. The intent is to install a well with a 40 HP well pump, this pump will need back up power. (It is not a fire pump)
It appears as if the 40 HP will not fit on the existing generator system. So we need to either replace the existing 75KW (they also have expansion plans and a low budget) or provide a dedicated emergency generator just for the well system.
Facilities stated to me that if we replace the 75 KW with a 125 KW they do not have to provide additional transfer switches, separate branches of power, and address the existing emergency system.
Has anyone heard this before, I have not? Certianly does not sound correct.
In general if we replace the 75 KW unit would we be required to bring the existing emergency system up to current code? Or can I replace the generator, provide 1 new equipment branch ATS and back feed the old ATS without separating the existing loads, etc.?
I have an existing hospital with an emergency generator nameplate rating of 75 KW and 260 amps. Monthly test show a peak of 210 amps recorded via facilities. 1 ATS with no separation of life safety, critical, equipment. 1 EM distribution panel that feeds everything. 1970 construction.
The Hospital has been forced to add a sprinkler system per the State. No domestic water available. The intent is to install a well with a 40 HP well pump, this pump will need back up power. (It is not a fire pump)
It appears as if the 40 HP will not fit on the existing generator system. So we need to either replace the existing 75KW (they also have expansion plans and a low budget) or provide a dedicated emergency generator just for the well system.
Facilities stated to me that if we replace the 75 KW with a 125 KW they do not have to provide additional transfer switches, separate branches of power, and address the existing emergency system.
Has anyone heard this before, I have not? Certianly does not sound correct.
In general if we replace the 75 KW unit would we be required to bring the existing emergency system up to current code? Or can I replace the generator, provide 1 new equipment branch ATS and back feed the old ATS without separating the existing loads, etc.?