I am currently working on a Data Center that is being designed around Article 645.
I have multiple exits out of the space that are double doors that have an EPO at the exit.
I have one location that has a mantrap (door from data center to small room then another door to the corridor). Per 645.10 it requires an EPO at the Principal exit doors.
Would we be required to add an EPO at the Mantrap door since it is exiting into another room and not an exit corridor?
645.10 Disconnecting Means A means shall be provided to disconnect power to all electronic equipment in the information technology room. There shall also be a similar means to disconnect the power to all dedicated HVAC systems serving the room and cause all required fire/smoke dampers to close. The control for these disconnecting means shall be grouped and identified and shall be readily accessible at the principal exit doors. A single means to control both the electronic equipment and HVAC systems shall be permitted. Where a pushbutton is used as a means to disconnect power, pushing the button in shall disconnect the power.
Thanks,
Ed
Thanks,
Ed