A anbm Senior Member Location TX Occupation Designer Apr 5, 2010 #1 50kVA UPS - 480V input, 480V output. Do we need to meet any code requirement for UPS installation - location wire? Can it be in any rooms if we meet clreance around the UPS and AC the room? Thanks!
50kVA UPS - 480V input, 480V output. Do we need to meet any code requirement for UPS installation - location wire? Can it be in any rooms if we meet clreance around the UPS and AC the room? Thanks!
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 5, 2010 #2 Does it feed or happen to be in an Information Tech room. If so you need the check Aty 645
chris kennedy Senior Member Location Miami Fla. Occupation 60 yr old tool twisting electrician Apr 5, 2010 #4 anbm said: Does not serve IT room/load. Click to expand... What does it serve?