I am trying to integrate a wind turbine into a diesel genset power system.
The turbine is 480v/285a induction machine. So I have a 400a breaker for it
(285*1.25=356).
Downstream of the turbine is a 300kva 480/208 dry type xfmer.
As I understand the NEC, Table 450.3(B) says that I have to have overcurrent protection for the primary of the xfmer. I have sized this to be 500A (300000/831=361*1.25=451).
My questions is this: I have a 400a breaker on one end and then a 500a on the other end. This just doesn't seem right.
Can anyone help?