Some useful information:
Insulation level applies to what?s referred to ------
QUOTE]
Very interesting explaination
See the below topic too
100 Percent Level,
Cables in this category may be applied where the system is provided with relay protection such that ground faults will be cleared as rapidly as possible, but any case within one minute. While these cables are applicable to the great majority of cable installations that are ground ed systems, they may be used also on other system for which the application of cables is acceptable provided the above clearing requirement are met in completely de-energizing the faulted section.
133 Percent Level,
This insulation level corresponds to that formerly designated for "ungrounded" systems. Cable in this category may be applied in those situations where the clearing time requirement of the 100 percent category can not be met, and yet there is adequate assurance that the faulted section will be de-energized in a time not exceeding one hour. Also, they may be used when additional insulation strength over the 100 percent level category is desirable
173 Percent Level,
Cables in this category should be applied on systems where the time required to de-energize a section is indefinite. Their use is recommended also for resonant grounded systems. Consult the cable manufacturer for insulation thickness.