BrianG

New member
We are installing a new 135V.DC 600Amp ungrounded distribution panel and am trying to size the equipment ground for the panel. I have not been able to find any guidelines in the NEC for this application. Our ground grid is 4/0 cu. Should we go with the NEC grounding requirements for an A.C. panel (this would be #1 cu.) ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Welcome

Best take a look at section VIII of Art 250 (pg 120 in the '08 Code)
there are a few "what ifs"

Afterward, if you have questions, ask us
 