I'm still unclear.
I'm bonding four service supply side conduits feeding a row of four 400A, 480v switches to building steel and to the water supply.
Each switch has three 500mcm conductors.
There is no grounded conductor.
1.) Building steel is close. The water line is 50 feet away. Do I need to run an individual 1/0 to building steel from each conduit (something someone said the other day seemed to indicate that) or can I hit each conduit grounding clamp with a single unbroken 1/0 and then exothermic to building steel?
2.) How then would or could I handle the conductor to the incoming water line?
a) if 4 individuals, then one 1/0 cadwelded to the same I-beam and then to the water line?
b) if only one conductor, can I tap with irreversible "C" from the 1/0 to the water line clamp?
3.) I assume the bonding lug to each can would be 1/0 and "C" tapped to the conductor leading to building steel
Thanks
I'm bonding four service supply side conduits feeding a row of four 400A, 480v switches to building steel and to the water supply.
Each switch has three 500mcm conductors.
There is no grounded conductor.
1.) Building steel is close. The water line is 50 feet away. Do I need to run an individual 1/0 to building steel from each conduit (something someone said the other day seemed to indicate that) or can I hit each conduit grounding clamp with a single unbroken 1/0 and then exothermic to building steel?
2.) How then would or could I handle the conductor to the incoming water line?
a) if 4 individuals, then one 1/0 cadwelded to the same I-beam and then to the water line?
b) if only one conductor, can I tap with irreversible "C" from the 1/0 to the water line clamp?
3.) I assume the bonding lug to each can would be 1/0 and "C" tapped to the conductor leading to building steel
Thanks