M mhernandez Member Location Chicago Apr 8, 2010 #1 What are the industry typical short circuit current ratings for panelboards, or swithboards buses? Thanks.
What are the industry typical short circuit current ratings for panelboards, or swithboards buses? Thanks.
zog Senior Member Location Charlotte, NC Apr 8, 2010 #2 mhernandez said: What are the industry typical short circuit current ratings for panelboards, or swithboards buses? Thanks. Click to expand... Can you be more specific? Voltage class? Vintage? You really mean SCCR or AIC?
mhernandez said: What are the industry typical short circuit current ratings for panelboards, or swithboards buses? Thanks. Click to expand... Can you be more specific? Voltage class? Vintage? You really mean SCCR or AIC?
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Apr 8, 2010 #3 mhernandez said: What are the industry typical short circuit current ratings for panelboards, or swithboards buses? Thanks. Click to expand... The bussing itself, is usually listed as 'maximum SCCR of XXXX, not to exceed the AIC of the actually installed breakers'.
mhernandez said: What are the industry typical short circuit current ratings for panelboards, or swithboards buses? Thanks. Click to expand... The bussing itself, is usually listed as 'maximum SCCR of XXXX, not to exceed the AIC of the actually installed breakers'.
M mhernandez Member Location Chicago Apr 8, 2010 #4 I'm talking about the panel bus, regardless of the breakers. Construction typicals.