mivey
Only because it is true. A single voltage by itself is a single phase. If we start trying to group them into systems of voltages then we start comparing the relative phase angle between the voltages. "Phase" has more than one meaning.That sounds like something mivey would say.
Great. You at least agree in part and recognize that there are three voltages. Oops, that means the "something mivey would say" above is also something jim dungar would say. The concept is the same.Just like I said about a two winding transformer which has two in-phase voltages, your transformer would have three single-phase voltages but not any poly-phase voltage.
As for in-phase voltages, I would agree: we have three single-phase voltages.
Now you are back to denying there are separate voltages. It looks like you are saying the wiring method is changing the number of voltages. Say it ain't so because you might find yourself saying something like mivey would say.When two or more of the windings are connected in series, the result is still a single phase voltage, although of a different magnitude.
Why are you saying the two voltages across the windings disappear when the windings are connected in series? The series connection made a 3rd voltage available, it did not dissolve the original two voltages.
If the neutral point has a wire that is a conductor, it makes a whole lot of difference.And if we care about the terminal relationships in order to connect these multiple windings together, then there is nothing wrong with using those terminal relationships when analyzing the resultant circuit, we should not need to change our methodology simply because a neutral point is created.
Without the neutral conductor, the current in both halves of the winding must be the same and you have only one voltage you can use. With a neutral conductor, the circuits using the winding halves can be different. Without the neutral conductor, we have one voltage to use. With the neutral conductor, we have two more voltages we can use.
Add: My methodology did not change. You can still apply the original rules and get the answer. Your method requires you to change the rules for specifically-identified cases.