wbalsam1
- Upper Jay, NY
A microwave receptacle is permitted to be a 15 ampere non-gfci- protected duplex receptacle in a kitchen area as long as it does not serve the countertop area. True? :-?
If it's up in the cabinet and not countertop, you betcha!
The receptacle may be able to be 15 amp but I'm guessing the circuit will need to be 20 amp. Check out the installation instructions with the microwave I'll bet they call out a circuit size. 1800 watts / by 120 volts = 15 amp and you can't load a receptacle to 100% on cord connected appliance. Just guessing at the 1800 watt part.![]()
You can if it is an individual circuit.
Read the opening paragraph of 210.23 again. It shows that Sub-sections (A) through (D) are to be applied to "A branch circuit supplying two or more outlets ..."210.23 (a) (1) may come into play, the OP did not say if it is "fastened in place" or not.
(1) Cord-and-Plug-Connected Equipment Not Fastened in Place. The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
What if it has a 15 amp plug?
Exactly. It is a cord-and-plug connection, not simply a receptacle. Manufacturers work in strange and mysterious ways, though.
