Harmonics through magnetic ballasts ??
powerplay
I was told that magnetic ballasts create harmonic current... does an inductive ballast add harmonics, or is the harmonics caused from an incorporated capacitor within ? I was under the impresion harmonics was more af an electronic issue.
Thanks again in advance!
100411-1452 EST
I looked at two different 8' Slimlines. These have quite different power factors. Both show substantial harmonic content on the current waveform. Both had a tendency to have three humps per half wave. If you did a slight running average the waveshape would be somewhat trapezoidal in shape.
At 122 V the readings using a "Kill-A-Watt" were
0.75 A, 81 W, 91 VA, 0.87 PF
0.95 A, 109 W, 117 VA, 0.94 PF
If you have or know someone with a scope and/or other instruments try some of your own measurements.
From Wikipedia
Some authors[1] define a trapezoid as a quadrilateral having exactly one pair of parallel sides, thereby excluding parallelograms.
100411-1521 EST
As an added point --- I think the power company might like this kind of load current to compensate for all the center peaked current from computers.
Later I will look at some combined waveforms.
This is another good area where readers might experiment.
100411-1710 EST
I have added an experiment:
The above results:
Both Slimlines on at once:
1.73 A, 196 W, 213 VA, 0.92 PF
A computer with a very peak current pulse:
0.66 A, 51 W, 81 VA, 0.62 PF
Then the combination of the three:
2.22 A, 256 W, 269 VA, 0.95 PF
Still a very bad current waveform.
Thus, the combined fluorescent improved the computer PF, and the computer improved the lamp PF.