e57
- San Francisco, CA
This thing is puny. 10k is not a lot... Even if the house is empty - what is it connected to? The 'idiot lights' - (which is what they are often reffered to - not implying you are...) may just be telling the truth - I would eliminate that first... Even if you may be there measuring voltage - one of two things could be happening while you're standing there.The manual lists the following problems that could cause a Low Voltage: restricted fuel flow, broken or disconnected signal lead, a failed alternator winding, control panel CB is open, generator is overloaded. Since the house is empty it can't be overloaded.
- Your meter is not fast enough to catch a voltage dip that the generator senses due to the applied load.
- The applied load that would cause a drop in voltage is/may be cycled in an 'off' state. Like a refer that is already cold, or a heater when it is already warm... Starting a motor too large, or doing so across a reduced or resistive connection could act very much the same way.
Then I would seek to replicate the problem while I'm there - and investigate that... Which set of controls is shutting it down - the transfer sw, or the generator? Focus on how that senses voltage.* Then go from there. Swapping parts until it works can only cost money and time.
And I'm sure you may have already called the manufacturer - they usually deal with the item in particular...
*FWIW I used to work on generators in the service, a few of them had some round about ways of sensing things - like 'engine speed' sensed by Hz - seems logical until something on the load changes the sensed Hz for reasons unrelated to actual 'engine speed'... Some flaws in air field lighting dimmers would knock out the generator due to 'over-speed'.
As far as connection issues go - WD-40 is not really a 'fix' - infact over time may do more harm than good. Is an oil, a dirt magnet, and does little to improve the connection once it drains away. Physically clean connections - flush with contact cleaner - repeat... Then coat the connection in dielectric or dielectric/silicone grease.