A corner grounded delta service can be designed for any desired voltage, but 240 is most common.
Only one voltage is available from such a system, there would be no choice of 120/240 or 120/208 or 277/480 as would be available from other service types.
The grounded corner will be the neutral and should be white or perhaps gray, no fuses or single pole switches or breakers may be inserted in this conductor, just as with any other neutral.
The two hot conductors may be coloured most any colour except white, grey or green, but red and black is very common.
In theory one could have a center tap on one or more of the windings, but this center tap COULD NOT be grounded, since one corner of the delta is already grounded.
With a 240 volt grounded delta and a center tap in one winding, it would be possible to obtain 2 wire 120 volt service with grounded neutral but this is very uncommon and not normally done.
With such a non standard and rare arrangement great care would have to be taken. For example if a 120 volt load was connected to the "wrong" end of the center tapped winding it would have 240 volts to ground and be potentialy dangerous.
I have heard of such services but they are very rare.
The usuall aplication is large, remote pumping stations that are either unmanned or very lightly manned. In such cases hundreds of HP will be required for pumping plant and for this a corner delata service is ideal.
Any small 120 volt 2 wire loads such as lighting or small appliances are supplied between the grounded corner of the delta and a center tap.
Some corner grounded deltas have center taps on all 3 transformers with nothing connected to the center taps. That is so as to use standard stock transformers intended for single phase 120/240 volt service.