314.23(F) Raceway supported enclosures, with devices, luminaires, or lampholders.
I clearly get this until I read the exceptions. Especially exception #2 and all of the conditions that have to be met in order for the exception to apply.
Basically the contractors are running 3/4 conduit down vertical I-beams on unistrut, and installing a mallable iron device box/enclosure for an exit sign. They are extending the box/enclosure anywhere from 20" to 24" past the last conduit support. I would like to see them install a "dead leg" nipple out of the bottom of these boxes and secure it to an additional unistrut support. Can someone help me clarify this? Thanks
I clearly get this until I read the exceptions. Especially exception #2 and all of the conditions that have to be met in order for the exception to apply.
Basically the contractors are running 3/4 conduit down vertical I-beams on unistrut, and installing a mallable iron device box/enclosure for an exit sign. They are extending the box/enclosure anywhere from 20" to 24" past the last conduit support. I would like to see them install a "dead leg" nipple out of the bottom of these boxes and secure it to an additional unistrut support. Can someone help me clarify this? Thanks